What happened at Fukushima (as of March 12, 2011)
The following is a summary of the main facts. The earthquake that hit Japan was several times more powerful than the worst earthquake the nuclear power plant was built for (the Richter scale works logarithmically; for example the difference between an 8.2 and the 8.9 that happened is 5 times, not 0.7).
When the earthquake hit, the nuclear reactors all automatically shutdown. Within seconds after the earthquake started, the control rods had been inserted into the core and the nuclear chain reaction stopped. At this point, the cooling system has to carry away the residual heat, about 7% of the full power heat load under normal operating conditions.
The earthquake destroyed the external power supply of the nuclear reactor. This is a challenging accident for a nuclear power plant, and is referred to as a “loss of offsite power.” The reactor and its backup systems are designed to handle this type of accident by including backup power systems to keep the coolant pumps working. Furthermore, since the power plant had been shut down, it cannot produce any electricity by itself.
For the first hour, the first set of multiple emergency diesel power generators started and provided the electricity that was needed. However, when the tsunami arrived (a very rare and larger than anticipated tsunami) it flooded the diesel generators, causing them to fail.
One of the fundamental tenets of nuclear power plant design is “Defense in Depth.” This approach leads engineers to design a plant that can withstand severe catastrophes, even when several systems fail. A large tsunami that disables all the diesel generators at once is such a scenario, but the tsunami of March 11th was beyond all expectations. To mitigate such an event, engineers designed an extra line of defense by putting everything into the containment structure (see above), that is designed to contain everything inside the structure.
When the diesel generators failed after the tsunami, the reactor operators switched to emergency battery power. The batteries were designed as one of the backup systems to provide power for cooling the core for 8 hours. And they did.
After 8 hours, the batteries ran out, and the residual heat could not be carried away any more. At this point the plant operators begin to follow emergency procedures that are in place for a “loss of cooling event.” These are procedural steps following the “Depth in Defense” approach. All of this, however shocking it seems to us, is part of the day-to-day training you go through as an operator.
At this time people started talking about the possibility of core meltdown, because if cooling cannot be restored, the core will eventually melt (after several days), and will likely be contained in the containment. Note that the term “meltdown” has a vague definition. “Fuel failure” is a better term to describe the failure of the fuel rod barrier (Zircaloy). This will occur before the fuel melts, and results from mechanical, chemical, or thermal failures (too much pressure, too much oxidation, or too hot).
However, melting was a long ways from happening and at this time, the primary goal was to manage the core while it was heating up, while ensuring that the fuel cladding remain intact and operational for as long as possible.
Because cooling the core is a priority, the reactor has a number of independent and diverse cooling systems (the reactor water cleanup system, the decay heat removal, the reactor core isolating cooling, the standby liquid cooling system, and others that make up the emergency core cooling system). Which one(s) failed when or did not fail is not clear at this point in time.
Since the operators lost most of their cooling capabilities due to the loss of power, they had to use whatever cooling system capacity they had to get rid of as much heat as possible. But as long as the heat production exceeds the heat removal capacity, the pressure starts increasing as more water boils into steam. The priority now is to maintain the integrity of the fuel rods by keeping the temperature below 1200°C, as well as keeping the pressure at a manageable level. In order to maintain the pressure of the system at a manageable level, steam (and other gases present in the reactor) have to be released from time to time. This process is important during an accident so the pressure does not exceed what the components can handle, so the reactor pressure vessel and the containment structure are designed with several pressure relief valves. So to protect the integrity of the vessel and containment, the operators started venting steam from time to time to control the pressure.
As mentioned previously, steam and other gases are vented. Some of these gases are radioactive fission products, but they exist in small quantities. Therefore, when the operators started venting the system, some radioactive gases were released to the environment in a controlled manner (ie in small quantities through filters and scrubbers). While some of these gases are radioactive, they did not pose a significant risk to public safety to even the workers on site. This procedure is justified as its consequences are very low, especially when compared to the potential consequences of not venting and risking the containment structures’ integrity.
During this time, mobile generators were transported to the site and some power was restored. However, more water was boiling off and being vented than was being added to the reactor, thus decreasing the cooling ability of the remaining cooling systems. At some stage during this venting process, the water level may have dropped below the top of the fuel rods. Regardless, the temperature of some of the fuel rod cladding exceeded 1200 °C, initiating a reaction between the Zircaloy and water. This oxidizing reaction produces hydrogen gas, which mixes with the gas-steam mixture being vented. This is a known and anticipated process, but the amount of hydrogen gas produced was unknown because the operators didn’t know the exact temperature of the fuel rods or the water level. Since hydrogen gas is extremely combustible, when enough hydrogen gas is mixed with air, it reacts with oxygen. If there is enough hydrogen gas, it will react rapidly, producing an explosion. At some point during the venting process enough hydrogen gas built up inside the containment (there is no air in the containment), so when it was vented to the air an explosion occurred. The explosion took place outside of the containment, but inside and around the reactor building (which has no safety function). Note that a subsequent and similar explosion occurred at the Unit 3 reactor. This explosion destroyed the top and some of the sides of the reactor building, but did not damage the containment structure or the pressure vessel. While this was not an anticipated event, it happened outside the containment and did not pose a risk to the plant’s safety structures.
Since some of the fuel rod cladding exceeded 1200 °C, some fuel damage occurred. The nuclear material itself was still intact, but the surrounding Zircaloy shell had started failing. At this time, some of the radioactive fission products (cesium, iodine, etc.) started to mix with the water and steam. It was reported that a small amount of cesium and iodine was measured in the steam that was released into the atmosphere.
Since the reactor’s cooling capability was limited, and the water inventory in the reactor was decreasing, engineers decided to inject sea water (mixed with boric acid – a neutron absorber) to ensure the rods remain covered with water. Although the reactor had been shut down, boric acid is added as a conservative measure to ensure the reactor stays shut down. Boric acid is also capable of trapping some of the remaining iodine in the water so that it cannot escape, however this trapping is not the primary function of the boric acid.
The water used in the cooling system is purified, demineralized water. The reason to use pure water is to limit the corrosion potential of the coolant water during normal operation. Injecting seawater will require more cleanup after the event, but provided cooling at the time.
This process decreased the temperature of the fuel rods to a non-damaging level. Because the reactor had been shut down a long time ago, the decay heat had decreased to a significantly lower level, so the pressure in the plant stabilized, and venting was no longer required.
***UPDATE – 3/14 8:15 pm EST***
Units 1 and 3 are currently in a stable condition according to TEPCO press releases, but the extent of the fuel damage is unknown. That said, radiation levels at the Fukushima plant have fallen to 231 micro sieverts (23.1 millirem) as of 2:30 pm March 14th (local time).
***UPDATE – 3/14 10:55 pm EST***
The details about what happened at the Unit 2 reactor are still being determined. The post on what is happening at the Unit 2 reactor contains more up-to-date information. Radiation levels have increased, but to what level remains unknown. |
|